The hospital operating room has high requirements for cleanliness, temperature, humidity, pressure and other aspects, and high requirements for stability. Therefore, the stability and reliability of the automatic control system is the first thing.
Based on many years of practical experience in the industry, JOLINE has launched an automatic control solution based on the operating room to realize the monitoring and management of operating room, advanced ward and equipment.
Name of operating room |
grade of operating room |
Minimum static pressure difference for adjacent low level cleanrooms |
temperature |
humidity |
Special clean operating room |
grade I |
+ 8PA |
22 ~ 25 ℃ |
40 ~ 60% |
Standard clean operating room |
grade II |
+ 8PA |
22 ~ 25 ℃ |
40 ~ 60% |
General clean operating room |
grade III |
+ 5pa |
22 ~ 25 ℃ |
35 ~ 60% |
Quasi clean operating room |
grade IV |
+ 5pa |
22 ~ 25 ℃ |
35 ~ 60% |